For the first time ever I am experiencing failures from a GRV-IDC24 module.
It started with a input failing, I then moved it to another input and it lasted a week or so then that also went. Changed the module, this worked for approximately 3 weeks and then also failed, moved the point, worked for couple of hours then failed again, moved to another and now working for 5 days with no failure
In the field I have a simple proxy sensor, connected to a 24VDC coil relay. On the N/O of the relay I bring a 24VDC supply from my power supply in the Groov panel and return it to the input on the GRV-IDC24 module.
Sensor is triggered, relay switches and input on Groov goes high.
When I measure the input voltage I get 24VDC, however when the relay switches this jumps to 30VDC then returns to the 24VDC.
Is there something I can place inline to stop these ports from packing up, eg a resistor ?
Assuming it is this slight surge that is causing it.
On the same line I have 2 of the same sensors, wired through the same make, type of relays in the same manner and they do not have this problem where the inputs fail. Only the one does this.
Is the NO contact and the IDC-24 the only “load” on the 24VDC power supply?
My guess is it could be poor output regulation on the supply or it the supply output is heavily inductive. Perhaps a small parallel dummy load on the supply that doesn’t get switched off may prevent a large spike (I bet the spike is a lot higher than 30VDC to be taking out the module). The IDC-24 current should be around 2-3mA at 24VDC, so a 20mA load should be good to see if the problem goes away. Or get a better power supply.
System is using approximately 8 inputs, and 8 outputs. All 24VDC.
Inputs consist of three proxy’s, limit, selector switch, push button and run signals from the motor contactors.
Output’s are wired from the ODC to a slimline single contact relay then to the field.
All are wired through a unshielded multicore to the main panel (11m), only place where it will be close to the robot and motor control is where it enters the bottom of the main panel.
Connected the the power supply permanently is a scale indicator. 24VDC
I had a Weidmuller DR-75-24 Power Supply in there and have now changed it to their PRO EC) 72W 24V 3A
Have used these components in combination in all my installations never to experience this. On another sight I am running 70 in and 64 out with no problems.
I therefore lean in favour of Beno’s assessment, ESD coming from somewhere in the field.
Therefore considering the route of:
Installing the TVSD on this channel that is causing the line failure
Linking my 0V to the GND line in the Groov Panel to eliminate any risk of floating
And then if it reoccurs replacing the unshielded cable with a shielded cable with the shield grounded on one end
Other option is to take my focus and work these points in reverse and try and eliminate the problem from the field starting with the shielded wire.