Thank you. I will check that out and report back what I find.
Returning to the subject of modbus serial with Node-RED using a USB-to-RS485 adapter plugged into the Rio (or EPIC), we have been successful in getting modbus data using node-red-contrib-serial-modbus
using these settings:
But since the above node has not been touched by the creator in over 2 years, I wanted to try the suite of modbus nodes in node-red-contrib-modbus:
specifically, the Modbus Read node is not able to connect
Here is how I have it configured:
I do not think it matters, but I do have the same node running successfully on another flow, but that is using Modbus TCP (whereas the above is using Modbus RTU).
Does anyone here have a working flow of the above node (Modbus Read) working with a Rio or EPIC? If yes, can you post your settings?
Hi @grant1 I am using those nodes with a USB to serial adapter on an EPIC to read a ModbusRTU power meter (Wattnode).
I am surprised that you don’t have a Unit-ID here in this config.
I might be wrong in needing to have the Unit-ID in both locations, but I did find that you need it where you don’t have it.
The next config is thus:
They look pretty good. I don’t think selecting RTU-Buffered is a make or break thing.
Hope that helps.
Thanks Ben. The slave address of my device is 11, so I set that as the Unit-Id on both settings screens. I know they mention ‘1’ and ‘set to empty’ in the Help, but I tried that as well.
Also, while you are using an EPIC and I am using a Rio, I noticed a few differences. I changed them both to match yours, and still no change in my debug pane.
#1: you are outputting the message from the second output (whereas I am outputting from the first output) of the modbus read node
#2: our serial port paths are different. Yours is /dev/ttyUSB0 and mine is /dev/ttySer0.
I think I got it. While setting up a brand new Rio, I did NOT have the old node-red-contrib-serial-modbus installed, and I am able to get the ‘green’ connection now. When it IS installed (but not even being used in a flow), it seems that both nodes are fighting over the serial / USB connection.
On a Rio or EPIC, how do I completely uninstall a node (or set of nodes) that are no longer needed? On a Pi or Debian box, I believe that is done thru terminal. Do I need to get SSH running to my Rio?
Removing nodes is the same as adding.
Just make sure they are not in any flows or have any configuration and then go into the node-red menu and remove them via the manage palette.
Thanks Ben. I knew to look to the Manage Palette menu, but the remove option was not there. I eventually got the remove button to appear by manually disabling in the menu shown in the second screenshot. All is good now and the node-red-contrib-modbus node is working its Modbus Magic.
Hello,
you have an example in the script, I try to write with function 16 to a single register, but, when executing it, it shows the error:
“TransactionTimedOutError: timed out”
Can you give us a little more information about what you are looking to do?
There is no script as I recall. Just a modbus node and a debug node.
Since you are getting a timeout error, your device address etc sound wrong, ie it cant access the modbus device.
Are you using serial or TCP?
I am using node-red in a groov RIO, I use a modbus reading node, I manage to read the value I want, but the refresh time is not stable, sometimes it takes a long time to read. these are the messages when starting the flow.
after a while, you can see the reading, but as I said before, time is not constant.
when trying to write a data in a register it generates an error,
this is my write node configuration:
can you help me how to write to a modbus register.
I also have this node installed, the result is the same, correct reading, but the writing fails.
I’m not seeing any errors in your debug output for your read nodes, seems fine.
Your write node is configured to write to 40006. Are you sure this is correct? Seems like just 6 would do the job based on your read node. If you have the debug nodes for the write display the full msg object you will probably see modbus error code 2 in there somewhere for invalid address.
hi,
You are right, it should be written in register 6 and not 40006, I don’t know what I was thinking at that moment, in the read register I wrote it correctly. but now the modbus 2 error appears and it is clearly an invalid or incompatible function.
I am using the other node, which, reading works perfectly. but writing throws me the following error.
Can you explain why you are switching nodes?
Did the write not work on the original node when you changed the address? Did you get the error 2 after changing the address or was this before changing the address? Does the device you are communicating with allow you to write to that register?
Edit: @beno, should this be moved into a separate thread so the original poster isn’t getting bothered with all the replies?
Can you explain why you are switching nodes?: because it throws me error 2, which indicates that there is an error in the requested function or the slave device is incompatible with said function (16). If I am wrong I would appreciate information.
Did the write not work on the original node when you changed the address?: no it didn’t work but this time as i reported earlier it says it doesn’t support feature 16
Did you get the error 2 after changing the address or was this before changing the address?: after changing address.
Does the device you are communicating with allow you to write to that register?: yes, it is a write register, try with register 5 and 7, but it doesn’t work either.
Exception code 2 is for an invalid address or quantity of registers. If the function code was not supported it should return with code 1.
If you want to use function code 6 instead of 16, that is an option with the node you were using before, though I don’t think that is the issue.
Are you sure you are trying to write to a single 16 bit register?
Can you share what the modbus device is and have a link to the documentation?
my mistake, if it’s code 1.
msg : error
“Error: Modbus exception 1: Illegal function (device does not support this read/write function)”
Did you try using function code 6?
yes, that’s how it works. it is function 16 that is not compatible with my equipment, use a modbus simulator with function 16 and it writes correctly. the limitation is on my computer and not on the node. thank you very much for your help.