Troubleshooting Node-RED Modbus issues
Can you explain why you are switching nodes?
Did the write not work on the original node when you changed the address? Did you get the error 2 after changing the address or was this before changing the address? Does the device you are communicating with allow you to write to that register?
Edit: @beno, should this be moved into a separate thread so the original poster isn’t getting bothered with all the replies?
Can you explain why you are switching nodes?: because it throws me error 2, which indicates that there is an error in the requested function or the slave device is incompatible with said function (16). If I am wrong I would appreciate information.
Did the write not work on the original node when you changed the address?: no it didn’t work but this time as i reported earlier it says it doesn’t support feature 16
Did you get the error 2 after changing the address or was this before changing the address?: after changing address.
Does the device you are communicating with allow you to write to that register?: yes, it is a write register, try with register 5 and 7, but it doesn’t work either.
Exception code 2 is for an invalid address or quantity of registers. If the function code was not supported it should return with code 1.
If you want to use function code 6 instead of 16, that is an option with the node you were using before, though I don’t think that is the issue.
Are you sure you are trying to write to a single 16 bit register?
Can you share what the modbus device is and have a link to the documentation?
my mistake, if it’s code 1.
msg : error
“Error: Modbus exception 1: Illegal function (device does not support this read/write function)”
Did you try using function code 6?
yes, that’s how it works. it is function 16 that is not compatible with my equipment, use a modbus simulator with function 16 and it writes correctly. the limitation is on my computer and not on the node. thank you very much for your help.