I would like to know if there is a product that could be used as a Point I/O (like the Allen Bradley Points I/O)
I am using this EPIC processor that must activate more than 30 valves that are like 30 feet away from the device. Another EPIC will not be the best solution. I am looking for this Point I/O so I can communicate with them through ethernet IP (or similar).
I wrote it wrong. The valves would be 300 feet away. Is there a way to use the 1734 Point I/O with PAC Control?
SNAP Pac and EPIC controllers must be installed with the I/O modules and they would not be used for the strategy. I am trying to run a single ethernet cable to the main controller.
It does not matter if its an EPIC or a SNAP at the valve end of the single Ethernet drop.
Both can be remote I/O to a PAC Control strategy running at the main controller.
You don’t need to run a strategy at the valves, but I think you should consider it. What happens if the Ethernet cable breaks? If you run a strategy at the valves, it can ‘safe’ the valves if communication is lost.