We are using Codesys v3.5 SP16 Patch-1 for Opto22 (GRV-EPIC-PR1) EPIC PR1.
We have mounted serial communication module (GRV-CSERI-4) and tiring to configure and create using Codesys but we couldn’t find library for Modbus serial communication.
We have downloaded the version 2.02.1 library from opto website and installed. But we couldn’t find and it’s not available Modbus serial communication Master/Slave library to configure. Pl check below screenshot for your reference.
Our demo also based on serial communication.
So Pl assist to us how to do this Modbus serial communication in codesys on urgent basis.
Hello there.
The Modbus is not part of the Opto library. It is another Codesys module you need to add.
I am not as up to speed on the Codesys library as @greichert is, he will be along shortly to help out.
I use the serial card with Modbus RS485 there is one quirk when using the codesys library (CODESYS Modbus Serial Master SL). The Opto22 PR1 modbus serial device definition does not exist. So, I added a codesys device that allows modbus serial (a raspberry pi); created the modbus master and slaves and then copy and pasted the modbus device into the PR1. It worked. You can test it out before buying the license from codesys. I think they just limit you to 2 hours.
They had provided ticket number. But they did not provided library file downloading link.
Where can we get that library file.?
I have activated that Modbus RTU Ticket (XXXX XXXX XXXX XXXX) in our device (GRV EPIC PR1). License also showing. But we couldn’t find any serial communication setting in Codesys v 3.5 SP16 Patch1 to configure.
This is good to know. We are new to Opto and from our team standpoint are more inclined to use Codesys.
We have taken over a lot of customers who are currently have SCADApacks using Modbus RTU over UHF radios on their remote sites with the master being located at their “office”.
They do not want to upgrade communications, but want hardware upgrades, so if the GRV-CSERI-4 can be used as master and slave we might have a fighting chance for integrating with the SCADApacks with the hope of one day getting rid of all the SCADApacks.
@reevesjj is correct, I verified this methodology, and made the development team aware of the current limitations, and a direct method will be added in future firmware.
Here is a quick way to get it into an EPIC Application:
I created a standard empty EPIC project:
I am wondering I the Modbus RTU issue ever got completely resolved for CodeSys on the Epic. @greichert , do you know? If so, could you provide a short ‘how-to’ on using the Modbus Serial library?
This has been fixed, you can add the modules directly to your device tree. Codesys Help site has a good overview of all the different combinations available for Modbus communications.