Can anybody help me figure out the way to read from and write to pac control via Ignition?
It seems that this feature has long gone
I’m using the latest firmware version of Epic with version 8.1.10 Ignition Edge, reason I upgrade because I need the BacNet driver from Ignition to communicate from a Device. Will really appreciate your help.
From there, your PAC Control tags will show up in designer - Well… to be clear, the PAC Control tags that you have checked the ‘Public Access’ option on…
Be sure and have only the tags / I/O that you want to make public checked. There is no need to check every tag in the strategy.
What I’m trying to do is use Ignition Edge to get BacNet data from a device and transfer/write the data into Pac Control variables via Ignition Designer
Garrick and I are chatting offline to figure the best way to guide you here.
Things changed with Ignition 8… Just give us a hot minute here…
Thanks.
EDIT. Ok it seems that because reasons Inductive removed the ability to associate OPC tags from within expressions tags in Ignition 8. You have to script it in j(p)ython or use the Compute module.
Garrick is going to write a new forum post like the old one you linked here (we don’t want this ‘how to’ to get buried in a slightly off topic thread).
While not really an Opto22 thing, we see the value in helping people move tags between Ignition modules so will write it up for all to use.