I am trying to connect from Groov View to a Modbus device without luck. I’ve test the port and IP in Groov Manage, and it’s open. But I can’t get the configuration of the tags right. I am using a stride IO module card for testing.
I did a Google search on that and am not sure which one are you meaning.
Can you link to a manual so a few of us here can try and figure out what magic combinations of check boxes and off by one and MSB byte order Modbus will need to talk to it… Thanks…
Can you also provide screenshots of your “Edit Modbus Device” screen in groov build (Configure, Devices and Tags…, select the modbus device and Edit Device button).
A screenshot of what you have attempted in Configure Tags for that device would be helpful as well.
The tag address is probably just 42 though (should show up as 400042 in groov view).
Whenever you see a modbus register with 400XX in the front, it usually just means it is a holding register and you drop the 4 part of it. This is the older style of representing addressing that was eliminated back in like 2006, but some companies are stuck in their ways…
Thanks for the help, i see to have a connection, but i am still not able to read the values as the device has. Maybe i am missing something, attached is the configuration on them.