I’m trying to read tags from Groov view to PLC IO.
Please suggest how to do.?
I’m trying to read tags from Groov view to PLC IO.
Please suggest how to do.?
If you want to read tags from a PLC into groov View, the PLC needs to support either OPC-UA or Modbus-TCP. groov View is then the Master (Client) to the PLC and will poll it.
In groov View you need to configure a new device as either OPC-UA or Modbus-TCP.
If your task is to move tags that you have in groov View from other sources to another Device (PLC), that is not possible. groov View does not have a Tag routing option. For this you can use Ignition Edge on EPIC and route tags between 2 devices. This will require a Igntion Edge license on the groov EPIC Controller.
There might be other options if you run groov View on an EPIC PR1/PR2 vial libraries in PAC Control or Codesys.