Good Morning,
I am a beginning user of PAC Control basic. I am trying to connect to a SNAP-PAC-EB2 brain and I am getting error code -10038. I CAN commmunicate to the the EB2 through PAC manager. I have identical IP settings in both applications. Any suggestions are appreciated
Ross
Welcome to the OptoForums! The part number you mention, the SNAP-PAC-EB2, is a brain (vs. a controller). You’ll need to download your “strategy” (the logic you’re writing in PAC Control basic) to a controller, which will then connect to the brain. You’ll configure the -EB2 in your strategy tree under “I/O Units” (vs. “Control Engines”).
The control engine can be: a SNAP-PAC-S series (controller only), SNAP-PAC-R series (both controller & brain), or SoftPAC (software controller that runs on a Windows PC). There’s also the free demo/trial subset of SoftPAC called “PAC Sim” which can also run on your Windows PC and talk to the -EB2).
This confusion between brain vs. controller happens a lot. If I’ve misunderstood where/when you’re seeing this error (I’m guessing it’s when you go to try to download/debug the strategy?) then let us know more details, and we’ll get you sorted out.
I encountered the same error code for a different reason. I had multiple NIC’s in my PC on the same subnet (I know, bad idea). The Opto22 controller was on NIC #3. When I attempted to reach it after some period of inactivity, I would get the -10038 error code two times as it first attempted communication on NIC #1, then NIC #2. On the third try, when it polled out on NIC #3, it would connect.
The problem was resolved by reassigning each NIC to its own subnet, which should have been done to begin with.