I have a small development system with 1 PR-1 (no I/O) and 3 EB1 I/O racks. All device ethernet connections are home runs to the network switch. In testing, if I disconnect one rack comm is lost to all racks and PR-1.
Re-connection starts all comm.
Have I missed something in the PR-1 configuration?
The PR1 is just like a SNAP controller, so there is nothing ‘special’ or different that needs to be done in PAC Control.
Each EB has a unique fixed IP address, the PR1 can have a fixed or DHCP IP address.
Each EB is configured in PAC Control with their IP address and whatever I/O modules are required.
Sounds like each EB is then wired back to a switch and the EB is also connected to that switch?
I wonder if you are using both Ethernet ports on the EB or if you are using Wifi or VPN? (Just wondering if there might be more than 1 gateway or subnet at play here).
Each EB has a static IP address and so does the PR1. All devices have only one ethernet port connected and an independent run to the network switch. No wifi, no VPN in a closed cell control network.
The PR-1 is at firmware 3.2.0-b.44 and the EBs are at 10.4c.
Just fyi - There is a redundant Snap S1 controller pair running on the same network, accessing different racks, all static IPs. Using a similar test only the rack that is disconnected goes offline and restarts when prompted to by the strategy.