Please post your comm handle string.
Also your modbus settings table values and the call to the modbus subroutine.
If you have a screenshot of the working values used in modbus poll, that would help too.
IIRC, -216 is the timeout error from the modbus kit.
Also - how were you connecting to the meter when using modbus poll? Were you going through the SCM module?