Setup: 2 groovEpic PR1 controllers
Controller A = Water Plant (169.254.1.3)
Controller B = Unit 2 (169.254.103.20)
Objective: Have Controller A Read data from Controller B’s Scratch Pad.
Configuring Controller B Scratch Pad:
I have the groovEpic’s local IO named Unit_01_Panel_01 set for Local (loopback)
Storing the data in Controller B’s Scratch Pad:
I have used this line of code:
stat_Write_Outputs_To_Scratch_Pad_Floats = SetIoUnitScratchPadFloatTable(Unit_01_Panel_01, 15, 452, 0, ft_Scratch_Pad_Float_Outputs);
Configuring Controller A to see Controller B’s Scratch Pad:
I created a Generic OptoMMP Device named Scratch_Pad_Unit_02_169_254_103_20 and assigned it the address of Controller B. (Does this need to be set for a Generic OptoMMP Device or should it be configured as a GRV-EPIC-PR1?)
Reading the data in Controller B’s Scratch Pad:
I have used this line of code:
stat_Get_Outputs_From_Scratch_Pad_Floats = GetIoUnitScratchPadFloatTable(Scratch_Pad_Unit_02_169_254_103_20,15,452,0,ft_Scratch_Pad_Float_Inputs);
Other than my question above does anything seem out of order?