Limitations of R1 with serial number lower than 600,000

It is the controller that is the limit, not the rack…
So, no matter what rack you use, controllers with serial numbers less than 600,000, ONLY the first 8 slots can have a mix of digital or analog.

In short, no, you cant put your eight allowed 4 channel modules just anywhere on the rack, they must be constrained to the first 8 positions.

Your guess is correct, no matter the rack, the connector on the bottom of those older controllers only has digital inputs for the first 8 positions.