Wrong analog in value reading in PAC disply

we are facing problem with our SNAP-PAC-R1 analog reading in PAC disply showing 110 psi with 4ma signal.Please advise how to resolve this issue.

Joby

what is the firmware version of the SNAP-PAC-R1 ?
try to update to 9.2a version

Joby,

We need a lot more information to help with this… for starters, does the value show up correctly in PAC Control in debug mode? if it is wrong there as well, then we need to know what module you are using, how it is wired, how it is scaled, etc. If the problem is really only in PAC Display, then try repairing tags.

Hi Joby,
Welcome to the OptoForums! You might want to contact our PSG (product support group) with troubleshooting help for this.
http://www.opto22.com/site/support.aspx
It’s FREE!
-OptoMary